Our insurance underwriter showed up unannounced. Four lessons.

Keith Nakamura
Director of Facilities · multi-site light industrial · Gwinnett / Cherokee
April 9, 2026
· 💬 0

Tuesday, 7:45 AM. I'm walking from my car to the building with coffee and a laptop bag and there's a guy in a polo shirt with a clipboard standing by the entrance. "Hi, I'm with [our carrier] — I'm the new loss control engineer for your account. Is this a good time?"

It was not a good time. But he was here, so it became a good time.

Four hours later he left. Here's what I learned.

Lesson 1: He looked at things I didn't expect

  • Extension cords. Any use of extension cords as permanent wiring. He found two. OSHA 1910.305. Not insurance code per se, but "if it's cited by OSHA it affects our loss ratio."
  • Storage against sprinkler heads. 18-inch clearance. We had pallets 12 inches from the deflector in the shipping corner. Photographed.
  • The fire extinguisher behind the forklift. Not blocked permanently, but "frequently inaccessible during operations." He drew a diagram.
  • Combustible storage in the mechanical room. Cardboard boxes stacked 6 feet high adjacent to the water heater. This one I should have caught. It's a standard exam-question item.

Lesson 2: He barely looked at the things I'd prepared for

I had sprinkler inspection reports, alarm test records, generator load tests, and SDS binders laid out in my office. He flipped through them in about 8 minutes total. "Looks fine."

What he spent 40 minutes on: the hot work program. Specifically, who signs our hot work permits, whether fire watches are documented with start/stop times, whether the fire watch coverage continues for 60 minutes post-work (NFPA 51B), and whether the permit covers contractor hot work or only employee hot work.

Answer was "sort of." We revised the program the following week. Hot Work Permit Generator saved me the typing.

Lesson 3: What the report said

Two "significant" findings (extension cords, combustible storage) and eight "recommendations." The way our broker explained it: significant findings can affect premium at renewal if unresolved; recommendations are flagged but not priced. Resolve both categories, don't let recommendations roll into significant at the next visit.

Lesson 4: How I prep differently now

  • Monthly self-audit using the same loss-control checklist he left me. First week of every month, facility manager walks his own building with the checklist.
  • Hot work program overhauled. Start/stop times logged. Fire watch training certificates on file. Contractor permits handled separately with a stricter review.
  • Storage audit weekly in shipping/receiving. Photos dated. If something's in the wrong place, we move it that day, not next week.
  • SDS binder access verified by actually trying to find a sheet for a randomly-named chemical. If it takes me more than 90 seconds, something's wrong.

The loss control visit was uncomfortable. It was also the single most useful audit we've had in three years — and I didn't pay a consultant for it.